Hello all. We have a system with two large 480Y/277V utility services feeding a large facility (two services are acceptable for our application per NEC 230.2 (C)). In addition, there are two generators to provide stand-by power (optional stand-by). There is a paralleling switchgear enclosure that houses the service disconnect circuit breaker for each service, a 3-pole tie circuit breaker section, and the circuit breaker for each generator (and the paralleling controls, ground fault detection, etc.). So the configuration is main-tie-main. And broadly, the intended operation is that the tie circuit breaker is normally open, and closes when neither of the services is available to turn on the generator(s). Since the tie circuit breaker is not 4-pole, the neutral is not switched, and per the NEC rules to prevent objectionable currents, we believe that the neutral must be bonded to the equipment grounding system only in the paralleling switchgear*, and not also at the generators. Everyone is kinda okay with this but the paralleling switchgear manufacturer has brought up the following point:
Per some of the standards that they use like UL 1581/891, and also to meet NEC 230.75, they will provide a neutral disconnect link in each of the service disconnect sections. And according to the manufacturer, UL 1581/891 requires them to provide the main bonding jumper connection on the line side of the neutral disconnect link**. Because the MBJ is on the line side of the NDL, when the neutral disconnect link is removed for the purpose of service and maintenance tests, etc., the generator neutrals will not have a connection to the equipment grounding system, if they install per our recommendation which is to not bond the generator neutrals to the generator cases (local grounding). The manufacturer has asked us to confirm we are okay with that kind of a scenario.
So the question is: is this thing a big deal? To me, it would seem like it is not. It would seem like if one disconnects the neutral to do some service/maintenance AND if one de-energizes the paralleling switchgear to do such service/maintenance, they should make sure the generators are not turned on too, and how much of a deal it would be to have the generators ungrounded for the duration of maintenance. If, on the other hand, the maintenance involves removing the neutral disconnect link AND testing while energized, then I am not sure what exactly to think of it. But it would still seem like the emphasis at that point should be on the fact that BOTH the services and the generators are commonly ungrounded (in the sense of "no connection of equipment ground") for the duration the testing is taking place, not that the generators are somehow uniquely handicapped/posing a problem to the system because of the lack of the neutral-ground connections for them. What are your thoughts on the matter? Given our 3-pole tie breaker that does not switch the neutral, it definitely seems like it is a no-go to provide local bonding at the generators AND in the paralleling switchgear (because the service neutrals must be grounded somehow too) as a way to address this potentially non-existent problem, and we definitely cannot eliminate the neutral disconnect links (which would be a violation of, among other things, 230.75), and also, per the manufacturer, we cannot connect the MBJs to the load side of the NDLs**.
Any help would be highly appreciated.
*The plan is to provide main bonding jumper in two places, one in each of the service disconnect sections, per 250.24 (C), without claiming 250.24 (C) Exception No. 1. Not 100% sure if this is the right approach. Maybe only one MBJ has to be provided in the paralleling switchgear (Exception No. 1 has to be claimed)? This is one of the other questions I have about this system.
**I do not have access to UL 1581/891 so I cannot personally verify this. But I have assumed it to be correct.
Per some of the standards that they use like UL 1581/891, and also to meet NEC 230.75, they will provide a neutral disconnect link in each of the service disconnect sections. And according to the manufacturer, UL 1581/891 requires them to provide the main bonding jumper connection on the line side of the neutral disconnect link**. Because the MBJ is on the line side of the NDL, when the neutral disconnect link is removed for the purpose of service and maintenance tests, etc., the generator neutrals will not have a connection to the equipment grounding system, if they install per our recommendation which is to not bond the generator neutrals to the generator cases (local grounding). The manufacturer has asked us to confirm we are okay with that kind of a scenario.
So the question is: is this thing a big deal? To me, it would seem like it is not. It would seem like if one disconnects the neutral to do some service/maintenance AND if one de-energizes the paralleling switchgear to do such service/maintenance, they should make sure the generators are not turned on too, and how much of a deal it would be to have the generators ungrounded for the duration of maintenance. If, on the other hand, the maintenance involves removing the neutral disconnect link AND testing while energized, then I am not sure what exactly to think of it. But it would still seem like the emphasis at that point should be on the fact that BOTH the services and the generators are commonly ungrounded (in the sense of "no connection of equipment ground") for the duration the testing is taking place, not that the generators are somehow uniquely handicapped/posing a problem to the system because of the lack of the neutral-ground connections for them. What are your thoughts on the matter? Given our 3-pole tie breaker that does not switch the neutral, it definitely seems like it is a no-go to provide local bonding at the generators AND in the paralleling switchgear (because the service neutrals must be grounded somehow too) as a way to address this potentially non-existent problem, and we definitely cannot eliminate the neutral disconnect links (which would be a violation of, among other things, 230.75), and also, per the manufacturer, we cannot connect the MBJs to the load side of the NDLs**.
Any help would be highly appreciated.
*The plan is to provide main bonding jumper in two places, one in each of the service disconnect sections, per 250.24 (C), without claiming 250.24 (C) Exception No. 1. Not 100% sure if this is the right approach. Maybe only one MBJ has to be provided in the paralleling switchgear (Exception No. 1 has to be claimed)? This is one of the other questions I have about this system.
**I do not have access to UL 1581/891 so I cannot personally verify this. But I have assumed it to be correct.