I have 3 sets of 500kcmil service conductors into main service disconnect MSB. The MSB main bonding jumper provided is #3/0 awg copper.

Engineer argument is table 250.66 note #2 applies and since their is no service entrance conductor the largest ungrounded conductor is 500 kcmil

Some how i think note #1 table 250.66 applies but their is no service entrance conductor.

Does anyone know in the above situation should MBJ be #3/0 awg or some other size? If other size then what and based on which code section table?
 
I have 3 sets of 500kcmil service conductors into main service disconnect MSB. The MSB main bonding jumper provided is #3/0 awg copper.

Engineer argument is table 250.66 note #2 applies and since their is no service entrance conductor the largest ungrounded conductor is 500 kcmil

Some how i think note #1 table 250.66 applies but their is no service entrance conductor.

Does anyone know in the above situation should MBJ be #3/0 awg or some other size? If other size then what and based on which code section table?
Note #1 is for "sets" which means each would feed a separate disconnect. Sounds like you have 3 conductors in parallel.

Can you be more specific about why there are - or you think there are - no service entrance conductors?
 
MBJs are sized by 250.102, not 250.66.
If you have parallel 500's,Cu, 3 per phase, then 3/0 would not be sufficient per Note 1 to Table 250.102(C)
 
Last edited:
If the 3 sets of 500's are in parallel your largest service entrance conductor is 1500 kcmil.
 
Note #1 is for "sets" which means each would feed a separate disconnect. Sounds like you have 3 conductors in parallel.

Can you be more specific about why there are - or you think there are - no service entrance conductors?

Service point is at the line side terminal of the main service disconnect
 
Service point is at the line side terminal of the main service disconnect
If you have 3 sets of 500 going into a main disconnect for the service then you have service conductors. The engineer is incorrect. Now a few code cycles ago the MBJ was sized the same as 250.66 but they moved the MBJ as well as other jumpers and grounded conductor to T250.102(C)(1)
 