I have 3 sets of 500kcmil service conductors into main service disconnect MSB. The MSB main bonding jumper provided is #3/0 awg copper.
Engineer argument is table 250.66 note #2 applies and since their is no service entrance conductor the largest ungrounded conductor is 500 kcmil
Some how i think note #1 table 250.66 applies but their is no service entrance conductor.
Does anyone know in the above situation should MBJ be #3/0 awg or some other size? If other size then what and based on which code section table?
Engineer argument is table 250.66 note #2 applies and since their is no service entrance conductor the largest ungrounded conductor is 500 kcmil
Some how i think note #1 table 250.66 applies but their is no service entrance conductor.
Does anyone know in the above situation should MBJ be #3/0 awg or some other size? If other size then what and based on which code section table?