MBJ

mannyb

Senior Member
Location
Florida
Occupation
Electrician
400a service 3/0 parallel copper . What size bonding jumper do you select from table. Is it #2 ? Because it's over 3/0 but under 350?
 
Since he actually said bonding jumper the correct table is 250.102(C). Calculation would be the same for a GEC.
 