Okay,securing and support is within every 6', unless connected to a fixture, and independent of the grid, cool.
Cables are secure and supported 1' from the fixture, correct?
My references for my questions:
300.11 Securing and Supporting.
(A) Secured in Place. Raceways, cable assemblies, boxes,
cabinets, and fittings shall be securely fastened in place.
Support wires that do not provide secure support shall not
be permitted as the sole support. Support wires and associated
fittings that provide secure support and that are installed
in addition to the ceiling grid support wires shall be
permitted as the sole support. Where independent support
wires are used, they shall be secured at both ends. Cables
and raceways shall not be supported by ceiling grids.
330.30 Securing and Supporting.
(A) General. Type MC cable shall be supported and secured
by staples, cable ties, straps, hangers, or similar fittings
or other approved means designed and installed so as
not to damage the cable
.
(B) Securing. Unless otherwise provided, cables shall be
secured at intervals not exceeding 1.8 m (6 ft). Cables containing
four or fewer conductors sized no larger than
10 AWG shall be secured within 300 mm (12 in.) of every
box, cabinet, fitting, or other cable termination.
(C) Supporting. Unless otherwise provided, cables shall
be supported at intervals not exceeding 1.8 m (6 ft).
Horizontal runs of Type MC cable installed in wooden
or metal framing members or similar supporting means
shall be considered supported and secured where such support
does not exceed 1.8-m (6-ft) intervals.