Hi all,
Bear with me for a moment, this seems a bit complicated (at least to me) and will try to give you a little background information.
The situation at hand involves a Smoke Control System wired with Fire Alarm type MC cable as the SLC (Signal Line Circuit).The fire protection specialist has indicated that according to the International Fire Code/International Building Code-which is their governing code for this large metropolitan area-that the SLC does not meet its provisions. It appears the violation has to do with IBC/IFC, Section 909 "Smoke Control Systems. Specifically, Section 909.12.1 which states the following "Wiring. In addition to meeting the requirements of the ICC Electrical Code, all wiring, regardless of voltage, shall be fully enclosed within continuous raceways.
I'm trying to come up with a rational code interpretation slanted towards utilizing the existing wiring in place and not have to remove it and put up a raceway, etc. I'd like to ask you guys if some of the things I found in the NEC make sense towards this goal.
First of all, as I understand it the ICC Electrical Code as of mid year 2008 was essentially replaced with the NFPA 70 (National Electric Code), except for some administrative appendices. Does anyone know if this is the case?
Furthermore, the way I read the NEC (Art. 100 Ch.1, pg 70-29) definition of a raceway, the Fire Alarm type MC cables continuous corrugated metallic sheath appears to meet this definition being both flexible and continuous or sealed.
Although, looking at NEC Art. 330 (7) ?In any raceway? this MC cable sheath is a raceway assertion is kind of contradicted. What are your thoughts on this?can the continuous corrugated aluminum sheath of the MC cable be considered a raceway??and if so, how can I make this argument?

Bear with me for a moment, this seems a bit complicated (at least to me) and will try to give you a little background information.
The situation at hand involves a Smoke Control System wired with Fire Alarm type MC cable as the SLC (Signal Line Circuit).The fire protection specialist has indicated that according to the International Fire Code/International Building Code-which is their governing code for this large metropolitan area-that the SLC does not meet its provisions. It appears the violation has to do with IBC/IFC, Section 909 "Smoke Control Systems. Specifically, Section 909.12.1 which states the following "Wiring. In addition to meeting the requirements of the ICC Electrical Code, all wiring, regardless of voltage, shall be fully enclosed within continuous raceways.
I'm trying to come up with a rational code interpretation slanted towards utilizing the existing wiring in place and not have to remove it and put up a raceway, etc. I'd like to ask you guys if some of the things I found in the NEC make sense towards this goal.
First of all, as I understand it the ICC Electrical Code as of mid year 2008 was essentially replaced with the NFPA 70 (National Electric Code), except for some administrative appendices. Does anyone know if this is the case?
Furthermore, the way I read the NEC (Art. 100 Ch.1, pg 70-29) definition of a raceway, the Fire Alarm type MC cables continuous corrugated metallic sheath appears to meet this definition being both flexible and continuous or sealed.
Although, looking at NEC Art. 330 (7) ?In any raceway? this MC cable sheath is a raceway assertion is kind of contradicted. What are your thoughts on this?can the continuous corrugated aluminum sheath of the MC cable be considered a raceway??and if so, how can I make this argument?