(mc) Miracle cable! Throw your benders away!!peter d said:Article 330. No maximum length....run it as far as you want. Check 330.30 for supporting and securing requirements.
Mule said:Please correct me if Im wrong but, alot of folks think that 6ft is the max that you can run flex or whips....Where this get mis guided is that IF you are going to utilize the flex for an equipment ground in leu of a ground wire, then 6ft is the max. Other wise if you have a equipment grounding conductor (EGC)pulled in the flex, then the limit does not apply.....
ItsHot said:(mc) Miracle cable! Throw your benders away!!![]()
Mule said:Please correct me if Im wrong but, alot of folks think that 6ft is the max that you can run flex or whips....Where this get mis guided is that IF you are going to utilize the flex for an equipment ground in leu of a ground wire, then 6ft is the max. Other wise if you have a equipment grounding conductor (EGC)pulled in the flex, then the limit does not apply.....
SEO said:Pay attention to art 300.11 complete article .
infinity said:OK since you asked I'll tell you that you are wrong. :wink:
There is a 6' maximum length associated with the use of 3/8" FMC whether you install an EGC or not. Look at 348.20(A)(2).
Thanks iwire glad you caught that.iwire said:Just an FYI 300.11 is a section not an Article. :smile:
Mule said:So my point would have been, (being better explained), would be 1/2" or larger with or without an EGC would be a factor in the 6ft length restriction???? right ? wrong?
infinity said:You still cannot use 1/2" of larger FMC without an EGC in lengths longer than 6'. There are also other restrictions. Take a look at 250.118(5).
infinity said:You still cannot use 1/2" of larger FMC without an EGC in lengths longer than 6'. There are also other restrictions. Take a look at 250.118(5).
steveng said:Rob, we have a ec doing a job for us who is using 3/8 mc with ground running in excess of 10' wiring light fixtures, the inspector allowed this work,
what specific article covers this exception? do you know?
am i understanding you correctly?
steve
steveng said:Rob, we have a ec doing a job for us who is using 3/8 mc with ground running in excess of 10' wiring light fixtures, the inspector allowed this work,
what specific article covers this exception? do you know?
am i understanding you correctly?
steve
348.20 Size.
(A) Minimum. FMC less than metric designator 16 (trade size ?) shall not be used unless permitted in 348.20(A)(1) through (A)(5) for metric designator 12 (trade size 3/8).
(1) For enclosing the leads of motors as permitted in 430.245(B)
(2) In lengths not in excess of 1.8 m (6 ft) for any of the following uses:
a. For utilization equipment
b. As part of a listed assembly
c. For tap connections to luminaires as permitted in 410.117(C)
(3) For manufactured wiring systems as permitted in 604.6(A)
(4) In hoistways as permitted in 620.21(A)(1)
(5) As part of a listed assembly to connect wired luminaire sections as permitted in 410.137(C)