Mc cable across the top or through joist?

Status
Not open for further replies.
NEVER put a hole in a joist, especially if the joist is also the bottom part of an engineered truss.

OK, there are exceptions, especially with TJI's. It's still best to avoid, unless you have no other choice. Even then, make sure to makethe hole round, and as small as possible, and place it where it does the least harm.
 
Can I run mc cable on the top of joist instead of drilling holes through the joist? Wood framing...

I would say that in general the answer would be yes. You might find some cases where this might not be acceptable like in an attic where it might be stepped on.
 