MC cable ampacity

Status
Not open for further replies.

blueheels2

Senior Member
Location
Raleigh, NC
Occupation
Electrical contractor
So reading around the general consensus is that the conductors in MC cable are THHN and are rated at 90 degrees. Terminations are usually rated 75 degrees so it limits Max cable to that ampacity. NEC 330.80 refers you to 310.60or 310.15 for ampacity. I don’t see anything in either of those that spells out that MC is good for 75. NM clearly states to use the 60!degree column. MC isn’t in any column. Is that because we are just using the internal conductors to figure allowable ampacity. What am I missing?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You would protect the conductors according to their ampacity in T310.16 but within the limits of 240.4. So for example even though #12 AWG is rated for 25 for amps at 75°C your still limited to the ampacity of 20 amps in 240.4 unless it meets 240.4(G).
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Unlike NM the conductors in MC are identified as THHN/THWN so you use the tables in 310.

Notice the conductor information in the specification section below.

 

blueheels2

Senior Member
Location
Raleigh, NC
Occupation
Electrical contractor