I am pulling a 100A feeder in MC Cable and I'm trying to find what size wire I need.
Following 330.80, directing me to T310.16, I believe I should follow 75 degree column which would be #4 (good for 85 amps / using 240.6 to up size breaker to 100)
am I correct in this?
Thank you
Following 330.80, directing me to T310.16, I believe I should follow 75 degree column which would be #4 (good for 85 amps / using 240.6 to up size breaker to 100)
am I correct in this?