MC cable and damp location

Status
Not open for further replies.

Telc

Member
It MC cable allowed exposed in the ceiling of a covered porch, if the wires are THWN? The wires would be rated for the location, and they wouldn't be subject to physical damage.
 
Take a look at 330.10. It appears to me that MC is permitted in damp locations and, even under certain conditions, in wet locations.
 
Thanks guys, I took a look at 330.10, the cable is non-pvc coated, but the conductors at THHN/THWN.
 
In the '08 FMC is not allowed in wet locations regardless of the type of wire inside of it per 348.12(1). I'm not sure that I would get to worked up about it under a covered porch, but that may be a question for the AHJ as many consider damp and wet the same thing.
 