mc cable and plastic busings

Status
Not open for further replies.

big mac

Member
Was it the intent of the code to make us use plastic bushings in metal studs when installing mc cable i have one electrical inspector making us use them.
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
Re: mc cable and plastic busings

Tom

300.4 Requires bushings in metal studs for type NM cable and ENT but not MC cable. Where are you seeing that they are required for MC cable?

[ May 19, 2003, 01:45 AM: Message edited by: curt swartz ]
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: mc cable and plastic busings

Dave,
The reference in 330.30(A) to 300.4 would permit the installation of the MC through the holes in the studs without out additional securing or supports.
Don
 

jbell59

Member
Location
Virginia
Re: mc cable and plastic busings

Curt:

I see 300.4(B1) where NM requires a bushing or grommet in metal studs but where is it stated for ENT?
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
Re: mc cable and plastic busings

jbell

I agree with you that they don't appear to be required to ENT. I didn't read 300.4 last night, I just posted from memory and I thought they were required for ENT. I'll have to look back through some old code books to see if this changed but maybe they never were required and my memory is going. I don't use much ENT in metal stud work but can tell you from experience that it is almost impossible to pull it through punched holes without using plastic bushings because the groves catch on the studs.
 

big mac

Member
Re: mc cable and plastic busings

The inspector was going by 330.17 and 300.4 he almost made us take the mc cable back out to put these in he finally let us the bushings to install them which also did'nt make any sense how do you get a ruling from the nec.
 

dana1028

Senior Member
Re: mc cable and plastic busings

What ruling could they give? There is nothing in 300.4(B)about MC... this section speaks specifically about NM and ENT... heck, it's entitled "NM & ENT through Metal Framing"...how much more clear can it be? If an inspector can't read, then he probably can't read the ruling either.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Re: mc cable and plastic busings

Dana, as section 330.17 (MC cable) refers you to 300.4, the rules of 300.4 apply to MC cable.
 

dana1028

Senior Member
Re: mc cable and plastic busings

I don't dispute 300.4(A) applies - this is the generic part of 300.4...it pertains to all cabling/wiring that gets too close to a wood stud edge.

However when you arrive at 300.4(B) (Metal Framing)it specifically names those wiring methods addressed in that code section - NM & ENT.

A,B,C breaks up the code into different sections - I believe the NEC Code Style Manual (?) makes reference to the layout of the code. An exception in (B)(1) does not apply to (A)(1). The reason a new section (B) was created was to differentiate the applicable rules between different wiring situations.
 