MC cable and voltage drop
MaxGlez
Guadalajara, Jal. Mexico
Aplication Engineer
Hello, good afternoon.
Im currently reviewing a project's single line diagram where there is a panelboard fed by a switchboard breaker with MC cable and want to do a voltage drop calculation, but i don't know what type of raceway to choose from Table 9, chapter 9 of the NEC to consider the effective impedance, can you help me out?
Thanks!
Every VD calculation I have done or seen doesn't use cable or raceway. The fault current calculators uses the raceway, I believe. Maybe somebody with more knowledge can be helpful
I did not use MC cable, but since the armor material is aluminum, I don't think it could change the magnetic fields and then the cable phase-to-phase reactance will remain unchanged with respect to non-armored cable. The steel conduit may change it [see NEC Table 9].
However, the resistance -due to losses in aluminum armor -it could be increased a bit mainly for large conductor cross section. In my opinion, we can use the aluminum conduit column for resistance.
I see what your saying. I'm use to using steel covered MC for feeders.
Using MC light may yield a different ansawer. Thing to watch for using AL is EMI. The steel provides better sheliding. So it really depends on the application. I have seen guys rip it out because they did not catch the spec. I should have mentioned that prior. Sorry
Thank you all for your answers: I think I agree the most with Mr. Right about using the aluminum conduit column, and in the case of a steel armor like Mr. Tulsa says, then we could the steel column. I have seen many times that table 8 is the one used for voltage drop calculations, but never agreed 100% with this because we're talking about AC current which has inductive and capacitive reactance (not the same with DC).
Best regards!
If you use the southwire calculator, it asks for your conduit type.