mc cable application?

Status
Not open for further replies.

lectro

Member
this is a question about the use of mc cable in health care facilities.when can you use regular mc cable vs.hcf type, especially as it relates to nursing home applications?i know that nec 517 and nfpa 99 apply to this situation,however as it pertains to nursing homes it seems to depend on the classification of the nursing home function.
 
Re: mc cable application?

the use of MC cable can apply if the sheath is a listed grounding conductor, check out 517.13(B) for grounding of receptacles and fixed equipment in patient care areas. Applies to nursing home, not limited care facility
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: mc cable application?

The interlocking armor type of sheath on MC cable is not listed for use as an equipment grounding conductor. There is no such thing as health care facilities MC cable. That cable is AC and not MC.
Don
 
G

Guest

Guest
Re: mc cable application?

The only products I found on that link were HCF AC. I did not find any HCF MC.

Can you provide a more direct link? Thanks!
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: mc cable application?

Health Care Facility Cable is not MC, period.

Many people generically refer to HFC as "hospital grade MC" but there is no such animal.

Roger
 

jhines

Member
Re: mc cable application?

You can talk with AFC's people. NEC 517.13(B) required the extra ground for "patient care." Patient care is defined in 517.2 and lists General care areas where patients come in contact with various items. If the nursing facility is assisted living with apartment style units and common dining, etc; MC is probably O.K. If medical assistance is provided in the unit, suggest using the extra ground.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: mc cable application?

Jhines, the issue is redundant grounding per 517.13(A) and (B)

There is no corrugated MC that would comply.

The ground strip in AC (517.13(A)) and HFC (A)and (B) accommodates this requirement.

If someone were to shop hard and found smooth MC it would also meet the requirement.

If the area is not under the 99 code, no flexible conduit or cable (excluding MI but you will probably have train everybody to use it) can be used for critical or life safety branches.

Roger

[ September 29, 2003, 04:33 PM: Message edited by: roger ]
 

tonyi

Senior Member
Re: mc cable application?

Originally posted by jhines:
Health care MC cable has extra ground. Look for type HCF, www.afcweb.com
If it has an internal bond wire and paper wraps, then its an AC type cable - you won't find either of these on an MC cable. HCF is an AC cable.
 

jhines

Member
Re: mc cable application?

Have not used it, but AFC "MC TUFF IG" with two ground wires is listed on page 2 as being for "517.13" AFC is 800-757-6996.
 

tonyi

Senior Member
Re: mc cable application?

Originally posted by jhines:
Have not used it, but AFC "MC TUFF IG" with two ground wires is listed on page 2 as being for "517.13" AFC is 800-757-6996.
Page 2 of what? The AFC web site makes a reference to article 518 (places of assembly) for this stuff, but I didn't see a 517.

Since this spiral tape MC's armor isn't suitable for a ground path, it can't possibly meet 517.13(A).
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: mc cable application?

Part of 517.13(A)
The metal raceway system, or cable armor, or sheath assembly, shall itself qualify as an equipment grounding return path in accordance with 250.118.
I agree with Tonyi even though MC IG has two copper grounding conductors it still does not meet the requirements of 517.13(A)
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: mc cable application?

Tony, you and I agree on your last post.

With out the cable assembly armor meeting 517.13(A), it wouldn't matter how many insulated bonding conductors are present, it wouldn't fly.

Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: mc cable application?

OK Bob, you beat me this time. ;)

Roger
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: mc cable application?

Don is smiling somewhere right now :)
The use of the term bonding conductor(s) seems even more appropriate in health care facilities although IMO it is better for all uses.

[ September 29, 2003, 08:34 PM: Message edited by: iwire ]
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: mc cable application?

Hi Bob and Ryan, I'm trying to discipline myself to use the correct term. I hope Don's proposal goes through.

Although, when I stumble don't flog me. :)

Roger
 

jhines

Member
Re: mc cable application?

You win, e-mailed the manufacturer, they have since removed their statement that their double ground MC was acceptable for medical.
 