MC cable connectors required?

Status
Not open for further replies.

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
My customer has fastened my stubbed out mc cables tightly as he installed sheet metal siding inside of warehouse. He wants me to surface mount outlet boxes. I'm fine with that except he securely fastened them, I had left a little play so I could install mc connectors on two cables and push them back a little so my box would fasten tight onto the wall. I'm glad he installed solid wood in each location, as I have a solid way to fasten my outlet box. But my question: is an mc cable connector required where the mc cable enters the back of a metal box ? Thank you.
 
Yes. I have used these successfully when the MC sheath ended at the wall:

images
 
My customer has fastened my stubbed out mc cables tightly as he installed sheet metal siding inside of warehouse.

Looks like it's on your customer to pay to make the necessary changes. What business did he have to do that??

How did he fasten them? Can you use a 3-1/2" hole saw to make a hole in the sheet metal behind where the box is going to go and then you could reach in and release the cables? Box would cover the hole.

-Hal
 
Thank you very much. My worker so far was able to oscillate tool through the steel and enlarge the hole, and found some loose play, and used 'two into one' mc connectors. Still more time than I had planned for.
 