I took a snapshot of this (see below). MC cable exposed throughout... Is this a violation?
If you think a violation, what do you suspect? Article and section?I took a snapshot of this (see below). MC cable exposed throughout... Is this a violation?
310.15(A)(2)Exception might negate any need for derating.From my understanding, if these have #12 conductors, then they should maintain adequate spacing if more than 20 current carrying conductors are jumbled up like that. Otherwise you would need to do 60% derating.
(4) Adjustment factors shall not apply to Type AC cable or to
Type MC cable under the following conditions:
a. The cables do not have an overall outer jacket.
b. Each cable has not more than three current-carrying
conductors.
c. The conductors are 12 AWG copper.
d. Not more than 20 current-carrying conductors are installed
without maintaining spacing, are stacked, or are supported
on “bridle rings.”
Clearly 'd' fails