I plan to penetrate a 3 hour fire rated wall with 3/0 - 3 conductor + ground MC cable.
I found a firestop submittal (see below and attached) which says this:
3. Cable bundle to be a combination of any of the following:
G. Maxmimum 3/C copper conductors no. 8 Awg metal clad cable
I. Any cables, metal-clad cable or armored cable currently classified under the through penetrating product category.
Why does it have 2 seperate conditions for "no. 8 cable" and "cables under the through penetrating products category"?
What does "through penetrating products category" mean? Does it mean it needs to be rated for fire rated penetrations?
Can I use 3/0 - 3 conductor + ground MC cable even if they say maximum allowed is #8 awg? The 3/0 cable I'm using is classified under the through penetrating products category I believe...