Then it's as you said in your first post, you only need to provide the proper supporting and it can be as long as the roll of MC you have.No, #12 MC Cable
In facilities where they want all wiring to be in conduit (RMC or EMT), it's pretty common to have a requirement like this written into the specs, limiting the length of flexible whips. But there's no Code requirement like this that I've ever heard of.What's the maximum length for a lighting whip using MC Cable? WVSFM is saying 6'. Looked at 330-30. Seems the only distance requirement is for supporting MC cable every 6'.
No, #12 MC Cable
(D) Unsupported Cables. Type MC cable shall be permit-
ted to be unsupported where the cable:
(2) Is not more than 1.8 m (6 ft) in length from the last
point of cable support to the point of connection to
luminaires or other electrical equipment and the cable
and point of connection are within an accessible ceil-
ing. For the purpose of this section, Type MC cable
fittings shall be permitted as a means of cable support