Hi! A contractor installed MC cable, enclosed in ceilings, walls and vertical ducts. They sized the wires according to Annex B Table B310.3, for MC cable on free air. Is that correct? Can those locations be considered free air? It is no placed on a cable tray, just BLine supports every 6ft.
Also, since that table is based on a 40C ambient temperature, they say can use the multipliers on the bottom of that table to increase the ampacity of the MC cables.
For example, they say average temperature is 21-25C, so they multiplied the Table B310.3 by 1.2.
I have the following concerns:
An MC Cable indoors/enclosed can be sized according to free air table?
Why use the tables on the Annex B and not the ones on 310?
If they use the 21-25C multipliers, what happens if actual ambient temperature is 33?
Thanks!
Also, since that table is based on a 40C ambient temperature, they say can use the multipliers on the bottom of that table to increase the ampacity of the MC cables.
For example, they say average temperature is 21-25C, so they multiplied the Table B310.3 by 1.2.
I have the following concerns:
An MC Cable indoors/enclosed can be sized according to free air table?
Why use the tables on the Annex B and not the ones on 310?
If they use the 21-25C multipliers, what happens if actual ambient temperature is 33?
Thanks!