MC cable in cable tray

Status
Not open for further replies.

cukele

Member
What are the derating factors and fill requirements for MC cables 600V or less in cable tray? The cable tray is aluminum, 9" rungs with a peaked solid cover.
 

cukele

Member
The cables are all 3 conductor #2 and smaller with mixed power and control. Will the rules of 392.9 apply?
 

cukele

Member
MC cable include.

MC cable include.

Neither 392.9 nor 392.11 specifically mention Metal-Clad cable, do the rules apply?
 

Smart $

Esteemed Member
Location
Ohio
Neither 392.9 nor 392.11 specifically mention Metal-Clad cable, do the rules apply?
MC is a cable, isn't it? Also see Table 392.3(A).

With only 3 conductors in your MC, there is no derating for number of conductors. Only ampacity adjustment is for ambient and 110.14(C) termination temperature limitations as applicable.
 