Just curious how many NEC violations people see with installing MC cable in this manner. I'm telling the EC to rip it all out for NEC violations and because our own specifications tell them to install rigid steel conduit for exterior, above ground, concealed installations. The black coating on the block is the vapor barrier.
View attachment 2037
I'm quoting these sections.
NEC 330.10(A)(11):
NEC 330.12(4): I'm not sure if cinder fill applies but there is mortar that dripped on the MC cable as the upper portion of the wall was constructed.
NEC 330.24: Bending Radius
Others? Or do people disagree with any of these?
View attachment 2037
I'm quoting these sections.
NEC 330.10(A)(11):
NEC 330.12(4): I'm not sure if cinder fill applies but there is mortar that dripped on the MC cable as the upper portion of the wall was constructed.
NEC 330.24: Bending Radius
Others? Or do people disagree with any of these?