Exception No. 2: Luminaires (light fixtures) more than 2.3 m (7 1/ 2 ft) above the floor and switches located outside of the patient vicinity shall not be required to be grounded by an insulated equipment grounding conductor.
17.13 Grounding of Receptacles and Fixed Electric Equipment in Patient Care Areas
Wiring in patient care areas shall comply with 517.13(A) and 517.13(B).
(A) Wiring Methods
All branch circuits serving patient care areas shall be provided with a ground path for fault current by installation in a metal raceway system, or a cable having a metallic armor or sheath assembly. The metal raceway system, or metallic cable armor, or sheath assembly shall itself qualify as an equipment grounding return path in accordance with 250.118.
(B) Insulated Equipment Grounding Conductor
The grounding terminals of all receptacles and all non?current-carrying conductive surfaces of fixed electric equipment likely to become energized that are subject to personal contact, operating at over 100 volts, shall be grounded by an insulated copper conductor. The equipment grounding conductor shall be sized in accordance with Table 250.122 and installed in metal raceways or as a part of listed cables having a metallic armor or sheath assembly with the branch-circuit conductors supplying these receptacles or fixed equipment.
Exception No 2: allows for excluding the insulated conductor required in 517.13(B), but does dot exclude any other part of article 517.13, so regular MC is not allowed in Patient Care Areas even above 7.5'
Roger
roger said:Trevor, the explanation of why the metallic raceway or sheath takes priority over a copper conductor can be found in Annex A of NFPA 99, which is at home right now.
I will try to post it this weekend.
Roger
There is no MC of the interlocking armor type that is suitable for this application.Sorry missed the regular MC part
The performance of the grounding system is made effective through the existence of the green grounding wire, the metal raceway, and all of the other building metal. Measurements have shown that it is the metal raceway and building steel that provide most of the effective ground path of less than 10 milliohms at the receptacle, including plug to receptacle impedance. The green grounding wire becomes a backup, not primary grounding path performer.