The 'common corrugated MC cable' has never been allowed in patient care areas.Originally posted by nd99:
Has the common corrugated MC cable been declared unsuitable for patient care areas since the 2002 NEC? Thanks.
when do you sleep?posted January 30, 2006 04:49
This would eliminate common interlocking MC as far back as then.The metal raceway system, or metallic cable armor, or sheath assembly shall itself qualify as an equipment grounding return path
No. See 517.13(A).Originally posted by Randazzo:
"MC" is allowable only if the connectors are approved as "suitable" for gounding. This can be found on the box or label the connectors came from.
This rules out the common, interlocked metal tape MC as a grounding coductor itself, and since the COMBINATION of the sheath and conductor is A equipment ground, those cables do not provide REDUNDANT grounding.The sheath of the smooth or corrugated tube type MC cable or a combination of the sheath and a supplemental bare or unstriped green insulated conductor is suitable for use as the required quipmenmt grounding conductor.