A question that I see asked fairly often on the forums is 'Can I run romex in conduit?' or 'Can I run MC in EMT?' etc. Often other posters will jump in with questions like 'Why would you do that?' or statements like 'That is too costly to do that.' or 'Its a waste of money.'
These exchanges have always surprised me as since I got in the trade as a teenager we have been doing that. It was how I was taught and how I still often do things.
So this past week I was doing an installtion of MC in raceway and I figured I could share it and generate some discussion about it.
The job was to wire some new HVAC equipment going on an outdoor pad. I had a 480V, 79A, 3PH unit, a 480V, 22A, 3PH unit a 120V 20A GFCI outlet and I included a 120V 20A spare.
The 480 had to come from the main electrical room about 225' away from the pad. The 120 I was able to get from about 75' away.
So here we go.
This first picture is at the electrical room end, this is 3/3 copper MC cable.
Below is inside the main electrical room, we ran about 15' of 1.5" EMT from the switchgear through the block wall and into the suspended ceiling.
Yes, at the other end of this pipe is a field made change over consisting of a 1.5" EMT set screw connector, a 1.5 GRC coupling and an MC connector. No box, no splice. Fast and easy.
Below is the outside of the building with the disconnects mounted at the new pad
Below are the cables stripped and ready to send outside. Very easy to strip of long sections if you do it in resonable size sections.
Here is the other end of all the cables as they head out through the block wall to outside the building.
Yes, that is solid 10 THHN being used to secure the cables to the strut that happened to be there.
In the photo below you can see we have pushed the cables outside.
And now complete.
I cannot see anyway that changing to THWN at each end would have made the job better or less costly.
These exchanges have always surprised me as since I got in the trade as a teenager we have been doing that. It was how I was taught and how I still often do things.
So this past week I was doing an installtion of MC in raceway and I figured I could share it and generate some discussion about it.
The job was to wire some new HVAC equipment going on an outdoor pad. I had a 480V, 79A, 3PH unit, a 480V, 22A, 3PH unit a 120V 20A GFCI outlet and I included a 120V 20A spare.
The 480 had to come from the main electrical room about 225' away from the pad. The 120 I was able to get from about 75' away.
So here we go.
This first picture is at the electrical room end, this is 3/3 copper MC cable.
Below is inside the main electrical room, we ran about 15' of 1.5" EMT from the switchgear through the block wall and into the suspended ceiling.
Yes, at the other end of this pipe is a field made change over consisting of a 1.5" EMT set screw connector, a 1.5 GRC coupling and an MC connector. No box, no splice. Fast and easy.
Below is the outside of the building with the disconnects mounted at the new pad
Below are the cables stripped and ready to send outside. Very easy to strip of long sections if you do it in resonable size sections.
Here is the other end of all the cables as they head out through the block wall to outside the building.
Yes, that is solid 10 THHN being used to secure the cables to the strut that happened to be there.
In the photo below you can see we have pushed the cables outside.
And now complete.
I cannot see anyway that changing to THWN at each end would have made the job better or less costly.