J jbolen Senior Member Aug 7, 2023 #1 I have a project where the contractor is wanting bundle the MC Cable in the Cable try. My understanding it had to be installed in a single layer.
I have a project where the contractor is wanting bundle the MC Cable in the Cable try. My understanding it had to be installed in a single layer.
L letgomywago Senior Member Location Washington state and Oregon coast Occupation residential electrician Aug 7, 2023 #2 jbolen said: I have a project where the contractor is wanting bundle the MC Cable in the Cable try. My understanding it had to be installed in a single layer. Click to expand... Is it running at its 90° Celsius rating?
jbolen said: I have a project where the contractor is wanting bundle the MC Cable in the Cable try. My understanding it had to be installed in a single layer. Click to expand... Is it running at its 90° Celsius rating?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Aug 7, 2023 #3 What size conductors? For #12 AWG you can bundle up to 20 CCC's with no derating.