VirutalElectrician
Senior Member
- Location
- Mpls, MN
- Occupation
- Sparky - Trying to be retired
I have a surplus of 2-2-2-6 MC cable that I'd like to use up for a sub panel. About 80' needs to go interior then about 30' underground.
The MC itself is not rated for burial, but the individual conductors are THWN.
According to the 2020 NEC, MC can be used in any raceway, and can be used in a wet location if the MC has a anti-corrosion coating and the individual conductors are rated for wet location.
It appears this is an acceptable configuration, except that the anti-corrosion coating requirement might be the sticking point.
Thoughts?
The MC itself is not rated for burial, but the individual conductors are THWN.
According to the 2020 NEC, MC can be used in any raceway, and can be used in a wet location if the MC has a anti-corrosion coating and the individual conductors are rated for wet location.
It appears this is an acceptable configuration, except that the anti-corrosion coating requirement might be the sticking point.
Thoughts?