MC Cable secured to sheetrock above grid ceiling

Status
Not open for further replies.

Johnhall30

Senior Member
Location
New Orleans, LA
Occupation
Engineer
Code opinions?

MC Cable secured to fire rated assembly above a grid ceiling, using 1/2'' EMT straps. (2) layers of 5/8'' sheetrock on underside of structural framing for a one hour assembly between 1st and 2nd floor. See picture below

The inspector says the MC cable must be above the sheetrock and ran within the joists.

I do not see anything in the NEC that would prevent this, and I believe the screws through the fire rated assembly do not compromise the fire rating per the IBC.
 