Code opinions?
MC Cable secured to fire rated assembly above a grid ceiling, using 1/2'' EMT straps. (2) layers of 5/8'' sheetrock on underside of structural framing for a one hour assembly between 1st and 2nd floor. See picture below
The inspector says the MC cable must be above the sheetrock and ran within the joists.
I do not see anything in the NEC that would prevent this, and I believe the screws through the fire rated assembly do not compromise the fire rating per the IBC.