MC Cable support clarification
69gp
MA
Hi just looking for some clarification on supporting MC cable.
330.30 (A) says that MC can be supported by cable ties.
110.12 informational note makes reference to ANSI/NECA 1-2006.
ANSI/NECA 1-2006 Section 9 (Q) says that cable ties shall not be used to support conduit and cable.
I can see using cable ties to hold the cables in place but not to support the full weight of the cable. (the cables in the picture are a 4 conductor 250 MCM MC). I can see over time the cable tie cutting into the MC jacket and allowing moisture into the cable.
Which is the correct section to follow?.
Finally how is it determined that a cable is to be protected from physical damage. In the picture below the MC cables are run at a right angle to the racking and are 6 to 8" above the ground. I say that these are subject to physical damage by someone stepping on them or someone possibly hitting them with a weed trimmer when the grass is being managed. Granted the site is fenced in but these are not qualified personnel maintaing the grounds. My feeling would be to have EMT or Rigid conduit
Informational notes are not code, they are just suggestions. An AHJ enforcing the NEC cannot cite an informational note as a requirement.
We use cable ties to support cables every day, what you do will be based on the customer specifications and your desires.
That is entirely up to the judgment of the AHJ or the inspector.
Sure it could happen, but is it likely? Arnt't these located under PV panels?
I don't see a weed trimmer hurting those cables in the least. It is worth remembering these cables also have waterproof conductors inside them.
Granted the site is fenced in but these are not qualified personnel maintaining the grounds. My feeling would be to have EMT or Rigid conduit
If EMT was in that same location and was stepped on it would also be subject to damage. I think the likelihood of conduits being stepped on is much greater than for cables. People expect a metal pipe to support them, they don't expect a cable to support them.
the cables are exposed for about 30" between the rows so it could easily be stepped on.
Also the commercial weed trimmers used today have a steel wire wrapped with nylon. So it is a lot stronger than the ones that had just the nylon. I think it will do a lot more damage.
That sounds like a shortcut that will be used for walking. If it was me I might run short sections of J-line, strut or even short sections of pipe to tie wrap the cables to at these crossings.
I cant even guess what the inspector will expect or not.
Could, might, maybe, if.
Not being a wise guy but that is what it always comes down to, it is an AHJ call as far as the subject to damage issue.
On the other hand the cable ties are directly allowed by code.
I'd be a little more concerned with the load those cables are placing on the cross strut. That's not Unistrut by any means and may not take that load over time.