Hi just looking for some clarification on supporting MC cable.
330.30 (A) says that MC can be supported by cable ties.
110.12 informational note makes reference to ANSI/NECA 1-2006.
ANSI/NECA 1-2006 Section 9 (Q) says that cable ties shall not be used to support conduit and cable.
I can see using cable ties to hold the cables in place but not to support the full weight of the cable. (the cables in the picture are a 4 conductor 250 MCM MC). I can see over time the cable tie cutting into the MC jacket and allowing moisture into the cable.
Which is the correct section to follow?.
Finally how is it determined that a cable is to be protected from physical damage. In the picture below the MC cables are run at a right angle to the racking and are 6 to 8" above the ground. I say that these are subject to physical damage by someone stepping on them or someone possibly hitting them with a weed trimmer when the grass is being managed. Granted the site is fenced in but these are not qualified personnel maintaing the grounds. My feeling would be to have EMT or Rigid conduit
330.30 (A) says that MC can be supported by cable ties.
110.12 informational note makes reference to ANSI/NECA 1-2006.
ANSI/NECA 1-2006 Section 9 (Q) says that cable ties shall not be used to support conduit and cable.
I can see using cable ties to hold the cables in place but not to support the full weight of the cable. (the cables in the picture are a 4 conductor 250 MCM MC). I can see over time the cable tie cutting into the MC jacket and allowing moisture into the cable.
Which is the correct section to follow?.
Finally how is it determined that a cable is to be protected from physical damage. In the picture below the MC cables are run at a right angle to the racking and are 6 to 8" above the ground. I say that these are subject to physical damage by someone stepping on them or someone possibly hitting them with a weed trimmer when the grass is being managed. Granted the site is fenced in but these are not qualified personnel maintaing the grounds. My feeling would be to have EMT or Rigid conduit