MC Cable Support

Alwayslearningelec

Senior Member
Location
NJ
Occupation
Estimator
Just curious as to how others would support. If you had a new construction space and had to get MC cables over to the blue box how would you supprt the cables above the hung ceiling if over 6'? I drew yellow lined to get semi visual.

I don't think the ceiling pencil rod would work for a Caddy type KX clip as that would be too late.

1721783729886.png
 

letgomywago

Senior Member
Location
Washington state and Oregon coast
Occupation
residential electrician
Can you get mulitple cables into one bridle ring? Do you usually need T-Rod dropped?
Multiple can go in. The MC types are bigger than the low volt type. If just a couple batwings are used on a t bar wire. If bridal ring is used either it needs to be on the framing members or on a 1/4in rod.

If using t bar wire they need to be for electrical only they can't use the ones for supporting the actual t bar grid but you can have extras shot in or screwed in for the electrical
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
He's referring to pencil rod so there will not be any T-bar wires.
Can you get mulitple cables into one bridle ring? Do you usually need T-Rod dropped?
Yes bridle rings come in many sizes up to 4". They can be attached directly to the slab or building steel (w/ beam clamp) without using threaded rod, although threaded rod is an option too.
 