Does anyone know of a NEC requirement prohibiting the installation of a 5KV MC cable and a 15KV MC cable in the same cable tray?
Thanks,
JS
Thanks,
JS
I see restrictions on mixed voltages in 392.20(B) and number of MV cables in 392.22(C) [2011], but no 392.6 at all. Did this change somewhere along the way?Your original post did not mention the presence of condcutors less than 600 volt, but if there are any present then there are restrictions as noted in 392.6(F). Also, if any of the conductors are service entrance conductors, there are restrictions in 230.44
No, the content is the same; Augie was citing 2008 or earlier.I see restrictions on mixed voltages in 392.20(B) and number of MV cables in 392.22(C) [2011], but no 392.6 at all. Did this change somewhere along the way?