m2oliva

Member
If the outside sheath of mc cable alone is not suitable for equipment grounding,if two mc cables are spliced inside a box,does'nt the ground insde the cables also have to be bonded to the box?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: mc cable

Then there must be 2 EGCs in the MC cable. One would connect to the metallic outlet box and the second to the grounding terminal on the receptacle.
Don
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: mc cable

m2oliva, The company I work for runs miles of this stuff.

We just ask for 12/2 IG MC or 10/2 IG MC.

This will show up with Black, White, Green and Green with Yellow stripe.

One maker of this cable is AFC Cable Systems out of New Bedford, MA, I sure there are others also.

AFC Cable Systems
 

m2oliva

Member
Re: mc cable

A couple more mc questions in regard to grounding .Must every outlet box have a pigtail to the box and to the outlet?If your splicing in a pullbox and there are numerous grounds from different circuits is it ok to put them all together and put one tail to the box[we useally keep one ground per 3 ckts.]
 