MC Cable

Status
Not open for further replies.

fifty60

Senior Member
Location
USA
Is MC cable permitted to pass through a class I div 1 location? I believe it is only permissible in a class I div 2 location, and that for class I div 1 wiring has to be ran in rigid or intermediate conduit..
 
Is MC cable permitted to pass through a class I div 1 location? I believe it is only permissible in a class I div 2 location, and that for class I div 1 wiring has to be ran in rigid or intermediate conduit..
Take a look at 501.10(A).
 
All Type MC-HL is rated for Class I, Division 1. NOT all Type MC is MC-HL though; it is a very specific construction.
 
Status
Not open for further replies.
Top