A ALPHA2 New member Location Melbourne, Fl. US Aug 22, 2018 #1 Can MC cable be ran exposed along an interior office wall feeding receptacles or lighting?
roger Moderator Staff member Location Fl Occupation Retired Electrician Aug 22, 2018 #2 Maybe, can it be considered subject to physical damage, if so the answer is no. See 330.10 and 330.12 for the specifics. Roger
Maybe, can it be considered subject to physical damage, if so the answer is no. See 330.10 and 330.12 for the specifics. Roger