hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have two 120V single pole breakers going to feed 120V single phase two separate loads.
Incoming is 208/120V three phase service to panelboard .
Plans show that they are using #1/4 MC + (1) #4 AWG gnd.
Questions:
1. Does MC cable come with equipment ground conductor or would it be outside the MC cable?
2. So 120V single phase require 1 phase, 1 neutral, 1 EGC. So 4-#1 MC have 3 phase conductors, 1 neutral or can MC cable come with 2 phase and 2 neutral and 1 equipment grounding conductor?
3. #2 I imagine neutral is shared. Has anyone wired how that works? Am I allowed to not use one phase at all of MC cable for two 120V single phase loads?
Incoming is 208/120V three phase service to panelboard .
Plans show that they are using #1/4 MC + (1) #4 AWG gnd.
Questions:
1. Does MC cable come with equipment ground conductor or would it be outside the MC cable?
2. So 120V single phase require 1 phase, 1 neutral, 1 EGC. So 4-#1 MC have 3 phase conductors, 1 neutral or can MC cable come with 2 phase and 2 neutral and 1 equipment grounding conductor?
3. #2 I imagine neutral is shared. Has anyone wired how that works? Am I allowed to not use one phase at all of MC cable for two 120V single phase loads?