scottysolar
Member
installing mc cable using short piece of rnc to ridgid 90 from ceiling box in concrete,using gal coupling and mc conn. ahj says this is violatation and needs access door at the conn with the 90 citing 300.15 any ideas
Why can't MC 90? connectors be concealed?walkerj said:If it is a 90 degree connector it can't be concealed.
chris kennedy said:Why can't MC 90? connectors be concealed?
Is it listed to be buried?scottysolar said:yes but why would you need accessability to a listed fitting
celtic said:Is it listed to be buried?scottysolar said:yes but why would you need accessability to a listed fitting
A straight FMC connector and a coupling can be pulled through without access.the same way a conduit coupling is listed to be buried ?
Ya think?scottysolar said:... def of fitting is locknut or bushing
Fitting.
An accessory such as a locknut, bushing, or other part of a wiring system that is intended primarily to perform a mechanical rather than an electrical function.
scottysolar said:type ac cable conn needs to be left accessible for inspecton of the antishort bushing. type mc cable does not need an antishort bushing therefore accessibility not required
My idea?scottysolar said:installing mc cable using short piece of rnc to ridgid 90 from ceiling box in concrete,using gal coupling and mc conn. ahj says this is violatation and needs access door at the conn with the 90 citing 300.15 any ideas