19clapshaw82
New member
My question is can an insulated throat mc connector like a 38ast be used on mc without a anti short bushing
I agree with the above. Also, check out the FAQ on this, but bear in mind: you will use antishorts on iwire's jobs, or you will go home.19clapshaw82 said:My question is can an insulated throat mc connector like a 38ast be used on mc without a anti short bushing
Pierre C Belarge said:The reason anti-short bushings (redheads) are not required for MC, is the design of the fittings for MC are such that when the MC cable is properly installed with the fitting, the fitting will provide the protection necessary.
I agree that it's not required but I don't agree with your assessment. . The fitting only provides protection for the conductor insulation against the rounded fitting edge. . It provides no protection against the freshly cut jagged edge of the MC jacket itself.
georgestolz said:I agree with the above. Also, check out the FAQ on this, but bear in mind: you will use antishorts on iwire's jobs, or you will go home.
brian john said:Not trying to start anything BUT how does that make a difference in the requirement issue? Or are you one of the many that would like to see antishorts in MC?
JUST CURIOUS
Antishorts, I prefer my men wear long pants to work, but I am not a members of the radical ANTISHORTS
Or are you one of the many that would like to see antishorts in MC?"
Nah ! . Just put me down as being a supporter of gouging the insulation with the cut jacket edge. . Let it short out and blow ! . I love fireworks ! . July 4th is great ! . If we get enough sparking then we'll have reason to add AFCIs to commercial circuits. . Why bother fixing the problem when you can just throw more money at it and they follow up with service calls for AFCI tripping ?
brian john said:I could not believe that anitshorts were not required when I first saw MC. BUT one on the primary functions I perform for this company is investigating neutral ground issues, to date I have seen none with MC. I have seen plenty with BX with and without anti shorts, mostly hacksaw cuts and BX connector screws piercing the insulation. Not saying it ain't going to happen, just have not seen to date.
"the primary functions I perform for this company is investigating neutral ground issues"
When they blow a hole in a 12gauge wire do you think they:
A) call you for an investigation
Once the wall gets tapped and painted, no one knows what happened ..... unless the short comes later on.
electricalperson said:a common practice around here is taking electrical tape and wrapping the end of it and using a romex connector. thats pretty hack in my opinion
Especially since a 2-screw romex connector and a 2-screw MC connector are within a penny of each other in price.electricalperson said:a common practice around here is taking electrical tape and wrapping the end of it and using a romex connector. thats pretty hack in my opinion
dnem said:When I go into a commercial project for an inspection and I see something like a 4"x4" or 6"x6" drywall patch above or below a box, I go over and take a peek. . When I see black powder streaks inside the box, I know what happened.
"the primary functions I perform for this company is investigating neutral ground issues"
When they blow a hole in a 12gauge wire do you think they:
A) call you for an investigation
or
B) just cut the wall open, do whatever it takes to repair it, and patch it up ?
Do you think they tell anybody that they used time and material to repair something on the backend instead of taking 2 seconds to slide in a plastic sleave on the frontend ?
Once the wall gets tapped and painted, noone knows what happened ..... unless the short comes later on.
76nemo said:This is another question of "above and beyond". I won't use MC w/o redheads. I do alot of machinery maintenance. I am a HUGE fan of bushings, redheads, cushioning. We don't service equipment with the intent for it to last for five years. Fifteen sounds more legit. I use anti-shorts and tape them. I like to use Arlington's push on's where not required. I also turn everything off in my house when not in use. Maybe I need help
anti-shorts and tape them
electricalperson said:a common practice around here is taking electrical tape and wrapping the end of it and using a romex connector. thats pretty hack in my opinion
electricalperson said:i use redheads whenever i use MC. and i make my helpers use them too and if they dont they go clean the truck
dnem said:The reason I hear that people skip using an antishort is TIME. . They don't want to take the extra one to 2 seconds to slide each one on.