jjc103 said:
Hi I'm new here but I was just wondering. I am wiring a small dental office. I know I must use a MC cable in the pstient procedure room in order to meet the requirements of a redundant grounding, but is it acceptable to use NM cable (romex) in the rest of the office. (waiting room, reception, hallways, file room, etc.).
Thank you
Not all MC cable qualifies for installation for patient care areas.
The standard MC cable that has been installed for years is not suitable as a wiring method for patient care areas. Check out Article 330.
From the UL White Book:
METAL-CLAD CABLE (PJAZ)
GENERAL
This category covers Type MC metal-clad cable. It is rated for use up to
2000 V, and Listed in sizes 18 AWG through 2000 kcmil for copper, 12 AWG
through 2000 kcmil for aluminum, or copper-clad aluminum, and employs
thermoset or thermoplastic insulated conductors. It is intended for installation
in accordance with Article 330 of ANSI/NFPA 70, ??National Electrical
Code?? (NEC).
The cable consists of one or more insulated conductors; one or more
grounding conductors (required for interlocked armor, as needed for smooth
or corrugated tube); one or more optional optical fiber members; and an
overall metal sheath. The metal sheath is an interlocked metal tape, a corrugated
metal tube, or a smooth metal tube. The metal sheath of singleconductor
cable is nonferrous. A nonmetallic jacket may be provided under
and/or over the metal sheath. Cable with metal armor, rated 5000 to 35,000
V is covered under Medium-voltage Cable (PITY) and is marked ??Type MV
or MC.??
Cable with interlocked armor that has been determined to be suitable for
use as a grounding means has interlocked aluminum armor in direct contact
with a single, full-sized, bare aluminum grounding/bonding conductor. This
cable is marked to indicate that the armor/grounding conductor combination
is suitable for ground. The equipment grounding conductor required
within all other cable with interlocked armor may be insulated or bare, may
be sectioned, and is located in the cable core but not in contact with the
armor. Any additional grounding conductors of either design have green
insulation. One insulated grounding conductor may be unmarked, one other
may have only a yellow stripe and the balance have surface markings that
indicate they are additional equipment grounding conductors or isolated
grounding conductors.
The sheath of the smooth or corrugated tube Type MC cable or a combination
of the sheath and a supplemental bare or unstriped green insulated
conductor is suitable for use as the ground path required for equipment
grounding . The supplemental grounding conductor may be sectioned.
When sectioned, all sections are identical. Each additional green insulated
grounding conductor has either a yellow stripe or a surface marking or both
to indicate that it is an additional equipment or isolated grounding conductor.
Additional grounding conductors, however marked, are not smaller
than the required grounding conductor.
PRODUCT MARKINGS
Information regarding temperature rating, voltage rating, cable and conductor
Type and AWG size is shown either on a marker tape under the
armor or on the surface of a nonmetallic jacket, if used.
Copper-clad aluminum conductors are surface printed ??AL (CU-CLAD)??
or ??Cu-clad Al.?? Aluminum conductors are surface printed ??AL.??
Cable employing compact-stranded copper conductors is so identified
directly following the conductor size, wherever it appears (surface, tag, carton
or reel), by ??compact copper.?? The abbreviations ??CMPCT?? and ??CU??
may be used for compact and copper, respectively.
Tags, reels and cartons for products employing compact-stranded copper
conductors have the marking: ??Terminate with connectors identified for use
with compact-stranded copper conductors.??
For termination information, see Electrical Equipment for Use in Ordinary
Locations (AALZ).
Cable suitable for use in cable trays, direct sunlight or direct burial application
is so marked. Cable marked for direct burial is also considered
acceptable for encasement in concrete.
Cable marked ??Oil Resistant I?? or ??Oil Res I?? is suitable for exposure to
mineral oil at 60?C. Cable suitable for exposure to mineral oil at 75?C is
marked ??Oil Resistant II?? or ??Oil Res II.??
Cable containing one or more optical fiber members is marked ??MC-OF.??
Cable with a nonmetallic outer jacket that complies with the Limited
Smoke Test requirements specified in UL 1685, ??Vertical-Tray Fire-
Propagation and Smoke-Release Test for Electrical and Optical-Fiber
Cables,?? and all unjacketed metal-clad cable may be marked with the suffix
??LS.??
Cable with an interlocked armor that is intended as a ground path is
marked ??armor is grounding path component,?? and is provided with installation
instructions.