Does the NEC proscribe fastening MC cable to the back side of steel stud framing? I know that inspectors, generally, want the the MC fastened to the face of the stud.
Does the NEC proscribe fastening MC cable to the back side of steel stud framing? I know that inspectors, generally, want the the MC fastened to the face of the stud.
300.4(D) Cables and Raceways Parallel to Framing Members
and Furring Strips. In both exposed and concealed
locations, where a cable- or raceway-type wiring method is
installed parallel to framing members, such as joists,
rafters, or studs, or is installed parallel to furring strips, the
cable or raceway shall be installed and supported so that the
nearest outside surface of the cable or raceway is not less
than 32 mm (11⁄4 in.) from the nearest edge of the framing
member or furring strips where nails or screws are likely to
penetrate. Where this distance cannot be maintained, the
cable or raceway shall be protected from penetration by
nails or screws by a steel plate, sleeve, or equivalent at least
1.6 mm (1⁄16 in.) thick.
Exception No. 1: Steel plates, sleeves, or the equivalent
shall not be required to protect rigid metal conduit, intermediate
metal conduit, rigid nonmetallic conduit, or electrical
metallic tubing.
Exception No. 2: For concealed work in finished buildings,
or finished panels for prefabricated buildings where such
supporting is impracticable, it shall be permissible to fish
the cables between access points.
Exception No. 3: A listed and marked steel plate less than
1.6 mm (1⁄16 in.) thick that provides equal or better protection
against nail or screw penetration shall be permitted.
it still needs support and securing. Tie wire is perfectwhat is on back side - if a concrete wall and there will be no access to the cable then what is there to protect it from besides ignorant inspectors.
it still needs support and securing. Tie wire is perfect
It was bit hard to understand but if as your thinking then the 1 1/4 rule appliesPersonally I think you have all misunderstood the question.:grin:
IMO he is asking about letting the NEC be 'inside' the open side of a metal stud instead of being on the face or flush side of the metal stud.
And i hope nec is typo for mc
Personally I think you have all misunderstood the question.:grin:
IMO he is asking about letting the MC be 'inside' the open side of a metal stud instead of being on the face or flush side of the metal stud.
Personally I think you have all misunderstood the question.:grin:
IMO he is asking about letting the MC be 'inside' the open side of a metal stud instead of being on the face or flush side of the metal stud.