MC Support

Status
Not open for further replies.
Location
MA
Had an open ceiling inspection yesterday that was shot down for the MC Cable not being Secured within 12" of the fixture. I referenced 330.30 (D)(2) (Unsupported cables) to the inspector and his reply was we didn't meet the requirements of 330.30 (B) since the wires weren't secured. Can anyone clarify if we are in violation? We have always used the 6' rule and never had an issue.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
This may help. It is showing AC but the wording is the same for both.

1008708069_2.gif


Roger
 

Strathead

Senior Member
Location
Ocala, Florida, USA
Occupation
Electrician/Estimator/Project Manager/Superintendent
Had an open ceiling inspection yesterday that was shot down for the MC Cable not being Secured within 12" of the fixture. I referenced 330.30 (D)(2) (Unsupported cables) to the inspector and his reply was we didn't meet the requirements of 330.30 (B) since the wires weren't secured. Can anyone clarify if we are in violation? We have always used the 6' rule and never had an issue.


I am confused. 330.30(B) starts out with "unless otherwise provided" does your inspector just ignore this?
 
Location
MA
He's arguing that although it states in 330.30(D)(2) that the cable doesn't need support if less than 6', it still needs to be secured in accordance with 330.30(B).
 

tkb

Senior Member
Location
MA
330.30(D)(2) states, Type MC cable fittings shall be permitted as a means of cable support.
he is wrong.
 

electricalist

Senior Member
Location
dallas tx
I agree the code is correct we have argued this same point.
How are the lights supported.? Ceiling wire is a must here so we bat wing to it and problem solved.
 
Location
MA
Funny you say that, we had used batwings and he gigged us for that too, I had to point out that the Massachusetts amendments allows you to attach to the ceiling ties if luminaries/equipment are supported by the ceiling. Walked into reinspection this afternoon with codebook open walked out watching tiles go in. Thank you all for your input
 

MasterTheNEC

CEO and President of Electrical Code Academy, Inc.
Location
McKinney, Texas
Occupation
CEO
Oh WAIT...didn't someone say that the conductors in the cable can only be 6' in length....lol......nevermind ...lol:angel:
 