When you say anything else, do you also mean the fixture support? I cannot find anything to supports your statement that does not allow this type of support. I did, however, find this. 410.16(C)Originally posted by chevyx92:
All the inspectors I've ever dealt with dont allow ceiling grid wire that supports the ceiling as a means of support for electrical wires or anything else for that matter.
Actually, you don't. At least, not according to the NEC. All that is required is that they are "securely fastened to the ceiling framing member by mechanical means such as bolts, screws, or rivets." (410.16(C))Originally posted by chevyx92:
When you set your troffers you have to tie them up with wire ....