• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

MC through stud bay return

Kimura

Member
Location
Delaware
Have read 330.22, but curious on something.

Is MC (something like Armorlite) permitted to run the length of a (cold air) stud bay return?
 
Last edited by a moderator:

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The code reference is 300.22(C). What is says is that the wiring method used in a plenum must be listed for use in plenums. Cables that are run perpendicular to the long dimension of the space are not required to be so listed. That would include NM cable.
 

kwired

Electron manager
Location
NE Nebraska
Occupation
EC
300.22(C)(1) specifically allows MC cable without an overall outer nonmetallic covering to be used in environmental air spaces.
 
Top