MC useage in firewalls

Status
Not open for further replies.

Flsparkey

New member
Location
Florida
Can you pass m/c cable into or thru a firewall if it is firestopped? This is a new partition in a office remodel and I am using m/c for most of the work above ceiling and in the walls. I think this would be more of a building code question.


Thanks guys.
 
Yes you can but, it will have to be fire stopped as an approved UL penetration or through penetration. You can find the approved assemblies in the UL Orange Books or, you can contact the particular manufacturer of the fire caulk you intend to use and let them give you their instructions. Of course you may have an inspector that will let you go if he/she sees some fire caulk around the MC. ;)


Roger
 
Yes you can but, it will have to be fire stopped as an approved UL penetration or through penetration. You can find the approved assemblies in the UL Orange Books or, you can contact the particular manufacturer of the fire caulk you intend to use and let them give you their instructions. Of course you may have an inspector that will let you go if he/she sees some fire caulk around the MC. ;)


Roger

That's usually what happens. Most contractors don't know how to intall fire caulk correctly and don't provide the proper paper work to the inspector.
 
That's usually what happens. Most contractors don't know how to intall fire caulk correctly and don't provide the proper paper work to the inspector.

I require all through penetration firestop systems to be submitted to our department so we now what they are useing and how they should be installing it.

Chris
 
I require all through penetration firestop systems to be submitted to our department so we now what they are useing and how they should be installing it.

Chris

I ask for it at plan check, but kind of hard to verify if the caulk goes back the depth of the drywall once it's been installed.

I hate when each trade does their own fire caulking, but out here we have a couple of companie's that's all they do. Very seldom that we have to check on them too hard, they usually tend to over do it and caulk where it's not needed.

I love when you point out a place they missed and they just tear off a piece of a pad and start to fix it with that.
 
Can you pass m/c cable into or thru a firewall if it is firestopped? This is a new partition in a office remodel and I am using m/c for most of the work above ceiling and in the walls. I think this would be more of a building code question.


Thanks guys.


2009 IBC 713.3.1
 