peterphamee
Member
- Location
- Alexandria, VA
- Occupation
- General Engineer
Is it correct MCA and MOP the same if a circuit breaker feeds only 1 motor? It's understood that MOP = (largest Motor FLA x 2.25 ) + motor 2 FLA + motor 3 FLA
MOP as defined by UL 1995 is applicable to HVAC load where there are more than 1 motor/s plus other loads (See UL 1995 Sec. 36.15). If your application is just a plain pump or fan, etc, the overcurrent protection recommended by NEC depends on the type of protection used and the type of motor/ duty it is intended for. For Induction motors being protected by Inverse time breakers, the factor is 2.5, not 2.25!Is it correct MCA and MOP the same if a circuit breaker feeds only 1 motor? It's understood that MOP = (largest Motor FLA x 2.25 ) + motor 2 FLA + motor 3 FLA