bradbb2005
Member
- Location
- South Carolina
- Occupation
- Electrical Designer
Hello,
I am having a discussion with our Mechanical Engineer on how things are shown on design drawings. Obviously, circuit sizing for HVAC equipment is driven by nameplate ratings per 440.4(B). When I am doing a design, I expect the mechanical engineer to provide these values based on a selected design basis, schedule them, then I, as the Electrical Designer show a schematic and circuit breaker matching their values.
He is basically saying he ends up calculating these values sometimes because he is unsure which model may get chosen in the end and cannot just pick one (we work in government work, most design-build (no our contractors don't get us selections ahead of time as you'd imagine)) and is hesitant to schedule the numbers because they may be incorrect. He ends up just scheduling a HP rating and is done with it.
On my end, without having an MCA or MOP design basis, I go back to sizing the circuit based on motor and load sizes, which also, in the end, may not match a selected piece of equipment's nameplate, which in turn shows incorrect sizing on the drawings compared to the actual selected unit.
It is my opinion that on HVAC equipment, Mechanical schedules a piece of equipment utilizing the MCA and MOP for the selected model and I design around that, at least the design drawings will be consistent and if the contractor selects a different piece of equipment, they would size accordingly or submit an RFI.
What are your thoughts on the subject and how have you come to an amicable agreement with Mechanical Designers / Engineers?
I am having a discussion with our Mechanical Engineer on how things are shown on design drawings. Obviously, circuit sizing for HVAC equipment is driven by nameplate ratings per 440.4(B). When I am doing a design, I expect the mechanical engineer to provide these values based on a selected design basis, schedule them, then I, as the Electrical Designer show a schematic and circuit breaker matching their values.
He is basically saying he ends up calculating these values sometimes because he is unsure which model may get chosen in the end and cannot just pick one (we work in government work, most design-build (no our contractors don't get us selections ahead of time as you'd imagine)) and is hesitant to schedule the numbers because they may be incorrect. He ends up just scheduling a HP rating and is done with it.
On my end, without having an MCA or MOP design basis, I go back to sizing the circuit based on motor and load sizes, which also, in the end, may not match a selected piece of equipment's nameplate, which in turn shows incorrect sizing on the drawings compared to the actual selected unit.
It is my opinion that on HVAC equipment, Mechanical schedules a piece of equipment utilizing the MCA and MOP for the selected model and I design around that, at least the design drawings will be consistent and if the contractor selects a different piece of equipment, they would size accordingly or submit an RFI.
What are your thoughts on the subject and how have you come to an amicable agreement with Mechanical Designers / Engineers?