This may seem like kind of a basic question but it is kind of critical.
I have an HVAC unit selection. According to the selection the unit has a MCA of 61 amps, MOCP of 70A. The voltage to the panel supplying this unit is 240-1. I need to turn this into kW for my panel schedules and load calcs.
Question: They list the MCA as 61.0 amps, the voltage listed on the selection is 230/1. When they figured the MCA of 61.0 amps, do you think they used 240 for a voltage or 230?
example:
240 * 61 = 14,640 watts
230 * 61 = 14,030 watts
Thats a difference of 610 watts. The panel is existing and is getting close to going over so I am counting every amp right now.
Thanks
See attached selection.