MCA v MOCP
Chamuit
Grumpy Old Man
Texas
I went to look at a job that was failed by an inspector. Two outdoor condensers.
First:
#10
20A MCA
30A Breaker
35A MOCP
Second:
#10
28A MCA
30A Breaker
45A MOCP
Inspector is saying that each unit MUST have a breaker matching the MOCP. I can't find anything in 440 that says I must use the Maximum OCP listed. Am I missing something here?
Neither unit has a minimum OCP.
First:
#10
20A MCA
30A Breaker
35A MOCP
Second:
#10
28A MCA
30A Breaker
45A MOCP
Inspector is incorrect. A maximum is never mandated.
Agreed - As long as breaker rating falls between the MCA and MOCP, it complies with Code. You may have some problems with nuisance tripping on the second 30A circuit though.
First:
#10
20A MCA
30A Breaker
35A MOCP
Second:
#10
28A MCA
30A Breaker
45A MOCP
The minimum for the circuit OCPD is the MCA so for #1 you need a minimum of a 20 amp circuit, #2 minimum of a 30 amp circuit. If #1 uses a 75° C wiring method like MC cable and 75° C terminals/equipment you could use #14 conductors with a 20, 25, 30 or 35 amp OCPD.
Thanks, guys. Just wanted to make sure I didn't miss something that had changed. :blink:
I had a conversation with the inspector and explained it exactly as y'all have to no avail.
I am going to go back and install a larger breaker on the second unit anyway for the reasons mentioned several times above.