I went to look at a job that was failed by an inspector. Two outdoor condensers.
First:
#10
20A MCA
30A Breaker
35A MOCP
Second:
#10
28A MCA
30A Breaker
45A MOCP
Inspector is saying that each unit MUST have a breaker matching the MOCP. I can't find anything in 440 that says I must use the Maximum OCP listed. Am I missing something here?
Neither unit has a minimum OCP.