Information from label on Grain Drying Equipment:
240V 3PH 60 Hz
218 Full load amps
70.2 largest motor amps. I am guessing this is nameplate data of the motor. There are two of these motors that start one after the other timed to allow the first to be at full speed before the next starts.
70.2 is not in table 430.250. Are they 25 hp @ 68A or a 30 hp @ 80A? Each * 1.25 = 87.5, 85 and 100 respectively.
I need to figure MCA of my feeder.
218-70.2=147.8 (all other loads which no doubt include motors that may also be using nameplate data instead of the table.)
Do I search each motor horsepower and recalculate load or use one of the calculated values above? Using the 30hp values would change my feeder size from 250kcmil cu to 300s. Parrallel is not an option due to lugs in dryer.