If you have a 300A breaker with #350's feeding a panel what size does the MCB in the panel need to be? Does it have to be at least 300A or could it be 250A?
IDK. But I guess it could be either???Does the customer want 300 amps or 250 amps available at the panel?
Other than it was a waste to size the conductors and upstream feeder for 300A…If you want to put a 250 Amp breaker downstream of a 300 Amp breaker with #350s between them, then you can do that. No issue
might not require a main CB at all.If you have a 300A breaker with #350's feeding a panel what size does the MCB in the panel need to be? Does it have to be at least 300A or could it be 250A?
Agree......unless voltage drop is an issue on the feeder.Other than it was a waste to size the conductors and upstream feeder for 300A…
I never use a Main breaker unless it serves some purpose such as for a tap rule or 408.36 issue. Some people seem to like the idea of a "local disconnect" but I don't see what that accomplishes.might not require a main CB at all.
Until you have to march 100 yards in a blinding snowstorm to reset the breaker in another building…I never use a Main breaker unless it serves some purpose such as for a tap rule or 408.36 issue. Some people seem to like the idea of a "local disconnect" but I don't see what that accomplishes.
If it's a separate building it will require a disconnect at the building (I know there is an exception, I've never used it).Until you have to march 100 yards in a blinding snowstorm to reset the breaker in another building…
...uphill both ways too!Until you have to march 100 yards in a blinding snowstorm to reset the breaker in another building…
What makes you think the main breaker will trip first?Until you have to march 100 yards in a blinding snowstorm to reset the breaker in another building…
Murphy’s Law…What makes you think the main breaker will trip first?
2023 NECIf you have a 300A breaker with #350's feeding a panel what size does the MCB in the panel need to be? Does it have to be at least 300A or could it be 250A?
2023 NEC and 2024 edition of NFPA 70E408.36 requires a panelboard be protected by a device having a rating no greater than then rating of the panelboard (bus).
That protection can be integral to the board or ahead of the board.
If your supply is protected by a 300 amp breaker and the panelboard is rated 300 amps, no additional protection is required.
If the panelboard is rated less than 300 amps then added protection based on that rating is needed,
.
Here in Texas you will need a main breaker, not an MLO (main lug only).
Thanks for reading
Comments accepted
TX+MASTER#4544
just like augie47 said in post #8.2023 NEC and 2024 edition of NFPA 70E
Texas
And if y'all conform to NFPA 70E, Standard for Electrical Safety in the Workplace it requires a remote disconnect or a MCB.
When reacting to a short circuit/ground fault, they both may trip.Murphy’s Law…