MCB Size
Alwayslearningelec
NJ
Estimator
If you have a 300A breaker with #350's feeding a panel what size does the MCB in the panel need to be? Does it have to be at least 300A or could it be 250A?
408.36 requires a panelboard be protected by a device having a rating no greater than then rating of the panelboard (bus).
That protection can be integral to the board or ahead of the board.
If your supply is protected by a 300 amp breaker and the panelboard is rated 300 amps, no additional protection is required.
If the panelboard is rated less than 300 amps then added protection based on that rating is needed,
2023 NEC
What is the panel's rating according to the label? You can't exceed the panelboard rating.
See 408.36 for your answer.
Here in Texas you will need a main breaker, not an MLO (main lug only).
Or it can be fed remote from a disconnect as an example.
Thanks for reading
Comments accepted
TX+MASTER#4544
2023 NEC and 2024 edition of NFPA 70E
Texas
And if y'all conform to NFPA 70E, Standard for Electrical Safety in the Workplace it requires a remote disconnect or a MCB.