If I’m looking at it correctly a 15kva step down(480 to 208v) xfrm puts out about 41 amps on the secondary side.
If I’m feeding a 120/208v panel on the secondary side would this 41 amps come into play when determining the panel MCB size or it would just be the loads the panel are feeding to determine the main breaker size?