Can you use a spare space in a mcc for anything other tgan a starter?
Sent from my iPhone using Tapatalk
Sent from my iPhone using Tapatalk
Our UL508 panel shop would routinely put power supplies, PLC's and other control equipment in spare MCC buckets.Can you use a spare space in a mcc for anything other tgan a starter?
Sent from my iPhone using Tapatalk
Good point. I did not mention that we would install a solid backpan and feed the installed components from a 120V circuit breaker in the factory installed lighting panel.You (or a UL508A panel shop) cannot build an MCC bucket with any power devices that would connect to the bus bars on your own and maintain the UL listing of the MCC. The UL listing of MCCs is under UL845, and there is no viable option for field assembled units, they must come from the factory. Panel shops can however make any modifications to control circuits in a factory assembled bucket under UL508A.
There is a program under UL2727 for some pre-qualified switchboard modification shops to make retrofit MCC buckets for obsolete MCCs. It is VERY expensive because of the documentation and possible testing involved. The only time I’ve seen people use this is when the gear is way too critical to abandon and hard to replace.
You can use the space, with an appropriate solid back pan and door, to house anything that is not directly connected to bus bars.