MCC as raceway

Status
Not open for further replies.

kenaslan

Senior Member
Location
Billings MT
Does anyone know the code section that prohibits the use of using a MCC as a raceway? Want to pass wiring through the bottom chase section into a 208V panel mounted on the other side of the MCC.

Thanks
Ken
 
Does anyone know the code section that prohibits the use of using a MCC as a raceway? Want to pass wiring through the bottom chase section into a 208V panel mounted on the other side of the MCC.

Thanks
Ken

430.97(A), unless your conductors are run horizontally only (sounds like they might be), and the conductors are isolated from the busbars by a barrier (easy enough).
 